Product and Software: This article applies to all Aruba controllers and ArubaOS versions.
Temperature Threshold Information
Aruba defines four temperature severity values: critical, major, minor and normal. Normal corresponds to any value less than the minor threshold. Install sufficient ventilation and cooling to facilitate operation within the normal temperature range at all times.
The following table shows the threshold values that are used to determine the severity of the temperature for each of the different Aruba controller models. Some models, such as the 3x00 and M3, have multiple sensors in multiple locations (potentially with different temperature ranges). Other models, such as the SC supervisor cards and 200 series, have only a single sensor.
In the following table, “AMP” denotes the Aruba Mobility Processor, which is an optional component on the M3 supervisor card. Where AMP is shown, the “CPU” sensor location is actually on the AMP FPGA, which is reported as “Mobility Processor” temperature in the ‘show inventory’ output.
MIPS-based XLR Systems (M3, 6xx, 3xxx)
Model |
Sensor Location |
Severity |
Temperature (° C) |
M3, AMP, 3x00, 620, 650 |
CPU |
Critical |
85.0 |
M3, AMP, 3x00, 620, 650 |
CPU |
Major |
80.0 |
M3, AMP, 3x00, 620, 650 |
CPU |
Minor |
70.0 |
M3, AMP, 3x00, 620, 650 |
CPU |
Normal |
< 70.0 |
|
|
|
|
M3, AMP, 3x00 |
card |
Critical |
72.0 |
M3, AMP, 3x00 |
card |
Major |
62.0 |
M3, AMP, 3x00 |
card |
Minor |
52.0 |
M3, AMP, 3x00 |
card |
Normal |
< 52.0 |
|
|
|
|
65x |
card |
Critical |
52.0 |
65x |
card |
Major |
44.0 |
65x |
card |
Minor |
39.0 |
65x |
card |
Normal |
< 39.0 |
|
|
|
|
620 |
card |
Critical |
60.0 |
620 |
card |
Major |
51.0 |
620 |
card |
Minor |
47.0 |
620 |
card |
Normal |
< 47.0 |
PPC-based Systems (200, 800, 2400, SC1, SC2, etc.)
Model |
Sensor Location |
Severity |
Temperature (° C) |
200 |
card |
Critical |
85.0 |
200 |
card |
Major |
80.0 |
200 |
card |
Minor |
70.0 |
200 |
card |
Normal |
< 70.0 |
|
|
|
|
All others |
card |
Critical |
60.0 |
All others |
card |
Major |
50.0 |
All others |
card |
Minor |
40.0 |
All others |
card |
Normal |
< 40.0 |
SNMP Traps
The same temperature thresholds are used for the generation of the wlsxOutOfRangeTemperature and wlsxNormalTemperature traps. If any temperature location exceeds its critical threshold value, a wlsxOutOfRangeTemperature trap is generated. After this trap is generated, the corresponding wlsxNormalTemperature trap is sent only when the temperature falls below the corresponding minor threshold.
SNMP Polling
Aruba controllers return an OID similar to the following format when the wlsxSystemExtMIB MIB is queried:
wlsxSysExtInternalTemparature.0 = STRING: 42.00 degrees Celsius (NORMAL)
The temperature value here represents the card temperature and the current temperature severity, based on the table of thresholds (indicated as NORMAL in this example). Note that if the controller has multiple temperature sensors, this OID returns only the card temperature.