Cable and cable plant are perhaps the most under-appreciated part of any network. Once run and connected, they are often forgotten about, sometimes for decades.
The problem is, sometimes they degrade or fail completely. A cable can look perfectly fine, but after one too many footsteps, office chairs, filing cabinets, rack doors, etc, it stops working as it should.
Like this one.
![2017-05-25 20.59.42.jpg 2017-05-25 20.59.42.jpg](https://higherlogicdownload.s3.amazonaws.com/HPE/MigratedInlineFiles/5f80c462a6cf46939bbb40d7bb40d31d_a286c0e4f98b48ffa23a3f4787ce5aba)
I needed to test a POE phone, so I plugged it in using the cable shamed in the picture above. It worked perfectly well for - as best I can estimate - over 15 years. It powers on the phone, but doesn't provide connectivity.
This is where the TDR (time domain reflectometer) comes into play. The TDR is built-in to most of the new Aruba-branded switches (previously known as ProCurve, E-Series, ProVision). That includes:
- 2930F
- the brand new 2930M
- 3810M
- 5400R V3 modules
I plugged both ends of the cable into a 2930M (yes, STP was configured properly), and ran these commands from the console.
2930M(config)# test cable-diagnostics 1/3-1/4
This command will cause a loss of link on all tested ports and will take
several seconds per port to complete. Use the 'show cable-diagnostics'
command to view the results.
Continue (y/n)? y
2930M(config)# show cable-diagnostics
Cable Diagnostic Status - Copper Ports
MDI Cable Cable Length or
Port Pair Status Distance to Fault
1/3 1-2 OK 5m
3-6 OK 4m
4-5 OK 5m
7-8 OK 4m
1/4 1-2 OK 5m
3-6 OK 0m
4-5 OK 4m
7-8 OK 5m
Note the "0m" for the 3-6 pair on port 1/4. Straight into the special box of broken bits used for testing and demos (after proper marking as "faulty" of course)!