HP A5800 JC100A temperature

This thread has been viewed 0 times
  • 1.  HP A5800 JC100A temperature

    Posted Jan 24, 2015 02:06 AM

    Dear All,

     

    I would like to ask about the given below pic. what does it mean of 44 C Temperature. this temperature of what. My server room temperature is 19 C , even switch is performing well. then why it is showing 44 C Temperature. Please help ...

     

     

    temperature.jpg

     

     

     


    #HPA5800Temperature
    #switches
    #coreswitch


  • 2.  RE: HP A5800 JC100A temperature

    Posted Jan 25, 2015 02:09 PM

    The switch has a psu and a couple of system cpus along with fpga/asics which all will generate heat when being used (thats why the unit have heatsinks and noisy fans).

     

    Hard to tell from your pic but if you login you can run:

     

    > display environment

     

    which will display something like:

     

    Slot 1
    System temperature information (degree centigrade):
    -------------------------------------------------------------------------------
    Sensor Temperature LowerLimit WarningLimit AlarmLimit ShutdownLimit
    hotspot 1 45 10 80 87 NA

     

    My interpretation is that this temp is the highest available within your unit (in my case its +45C where the surroundings are about +20C).

     

    In the above unit (HP 5820X-24XG-SFP+) you can see that the recommended maxtemp is +80C. So as long as the tempsensor reports below +80C everything is fine. However you want usually to have a margin to recommended maxtemp.



  • 3.  RE: HP A5800 JC100A temperature

    Posted Jan 27, 2015 08:01 PM

    When I first setup 5800s, I also noticed the high temperature and I also wondered if it was normal.



  • 4.  RE: HP A5800 JC100A temperature

    Posted Jan 28, 2015 03:58 AM

    Good question.

     

    What is "normal"? I don't have a clear answer.

     

    I can however give you some examples.

    1:

    HP7510 (MPU  LSQ1SRP2XB in slot 5, and LSQ1GP48SC in all linecard slots) Running Comware 5.20.105, R6708P08

    In a badly cooled room . Room temperature approx 32C

    ]display evironment

     

    System temperature information (degree centigrade):
    ----------------------------------------------------------------------
    Slot Sensor Temperature Lower Warning Alarm Shutdown
    0 hotspot 1 47 0 80 97 NA
    1 hotspot 1 43 0 80 97 NA
    2 hotspot 1 45 0 80 97 NA
    3 hotspot 1 44 0 80 97 NA
    4 hotspot 1 44 0 80 97 NA
    5 hotspot 1 37 0 80 97 NA
    7 hotspot 1 42 0 80 97 NA
    8 hotspot 1 42 0 80 97 NA
    9 hotspot 1 42 0 80 97 NA
    10 hotspot 1 41 0 80 97 NA
    11 hotspot 1 42 0 80 97 NA
    12 hotspot 1 30 0 80 97 NA

     

    here slot 5 and 12 are "the same" (the MPU) and it must have 2 different sensors. The other boards (all the same) vary from 47C to 41C which is either due to bad airflow, badly calibrated sensors, or different load on the boards, but you get the generel idea.

     

    2:

    HP7510 (MPU  LSQ1SRP2XB in slot 5, and LSQ1GP48SC in all linecard slots) Running Comware 5.20.105, R6708P03

    In a better cooled room . room temperature approx 24C

     

    ]display evironment

     

    System temperature information (degree centigrade):
    ----------------------------------------------------------------------
    Slot Sensor Temperature Lower Warning Alarm Shutdown
    0 hotspot 1 33 0 80 97 NA
    1 hotspot 1 36 0 80 97 NA
    2 hotspot 1 37 0 80 97 NA
    3 hotspot 1 37 0 80 97 NA
    4 hotspot 1 35 0 80 97 NA
    5 hotspot 1 28 0 80 97 NA
    7 hotspot 1 34 0 80 97 NA
    8 hotspot 1 35 0 80 97 NA
    9 hotspot 1 37 0 80 97 NA
    10 hotspot 1 35 0 80 97 NA
    11 hotspot 1 37 0 80 97 NA
    12 hotspot 1 30 0 80 97 NA

     

    The software patchlevel in 1: and 2: differs, but otherwise the units are the same - and have approximately the same load.

     

    On my comware 7 devices the limits are diffent:

     

    HP-5130-24 running  Comware 7.1.045, R3106

    in an office environment (guessing 24C or something)

    ]display environment

     

    System temperature information (degree centigrade):
    ----------------------------------------------------------------------
    Slot Sensor Temperature Lower Warning Alarm Shutdown
    1 hotspot 1 51 0 92 102 NA
    1 hotspot 2 55 0 98 108 NA
    1 hotspot 3 32 -20 63 70 NA
    1 hotspot 4 25 0 110 130 135

     

    not sure where those 4 hotspots are.

     

    HP5900, Comware Version 7.1.045, R2311P04

    in an office environment (guessing 24C or something)

    ]display environment

     

    System temperature information (degree centigrade):
    -------------------------------------------------------------------------------
    Sensor Temperature LowerLimit WarningLimit AlarmLimit ShutdownLimit
    hotspot 1 36 0 50 55 NA
    hotspot 2 46 0 58 63 NA

     

    so, different limits of course dependig on the ASICs and CPUs on the diffenrent boards.

     

    Hope this helps.

     

    Regards



  • 5.  RE: HP A5800 JC100A temperature

    Posted Feb 08, 2015 11:32 PM

    Thanks for your help and interest.

    this is the following temperrature table . 

     

    Capture.JPG

    so according to this temperature table . 47C consider as a normal and 80C will be consider as a over heated.



  • 6.  RE: HP A5800 JC100A temperature

    Posted Feb 14, 2015 07:03 AM

    Yeah and at +70C its time to take actions to fix the heat issue.

     

    So having +47C is "normal".