Good question.
What is "normal"? I don't have a clear answer.
I can however give you some examples.
1:
HP7510 (MPU LSQ1SRP2XB in slot 5, and LSQ1GP48SC in all linecard slots) Running Comware 5.20.105, R6708P08
In a badly cooled room . Room temperature approx 32C
]display evironment
System temperature information (degree centigrade):
----------------------------------------------------------------------
Slot Sensor Temperature Lower Warning Alarm Shutdown
0 hotspot 1 47 0 80 97 NA
1 hotspot 1 43 0 80 97 NA
2 hotspot 1 45 0 80 97 NA
3 hotspot 1 44 0 80 97 NA
4 hotspot 1 44 0 80 97 NA
5 hotspot 1 37 0 80 97 NA
7 hotspot 1 42 0 80 97 NA
8 hotspot 1 42 0 80 97 NA
9 hotspot 1 42 0 80 97 NA
10 hotspot 1 41 0 80 97 NA
11 hotspot 1 42 0 80 97 NA
12 hotspot 1 30 0 80 97 NA
here slot 5 and 12 are "the same" (the MPU) and it must have 2 different sensors. The other boards (all the same) vary from 47C to 41C which is either due to bad airflow, badly calibrated sensors, or different load on the boards, but you get the generel idea.
2:
HP7510 (MPU LSQ1SRP2XB in slot 5, and LSQ1GP48SC in all linecard slots) Running Comware 5.20.105, R6708P03
In a better cooled room . room temperature approx 24C
]display evironment
System temperature information (degree centigrade):
----------------------------------------------------------------------
Slot Sensor Temperature Lower Warning Alarm Shutdown
0 hotspot 1 33 0 80 97 NA
1 hotspot 1 36 0 80 97 NA
2 hotspot 1 37 0 80 97 NA
3 hotspot 1 37 0 80 97 NA
4 hotspot 1 35 0 80 97 NA
5 hotspot 1 28 0 80 97 NA
7 hotspot 1 34 0 80 97 NA
8 hotspot 1 35 0 80 97 NA
9 hotspot 1 37 0 80 97 NA
10 hotspot 1 35 0 80 97 NA
11 hotspot 1 37 0 80 97 NA
12 hotspot 1 30 0 80 97 NA
The software patchlevel in 1: and 2: differs, but otherwise the units are the same - and have approximately the same load.
On my comware 7 devices the limits are diffent:
HP-5130-24 running Comware 7.1.045, R3106
in an office environment (guessing 24C or something)
]display environment
System temperature information (degree centigrade):
----------------------------------------------------------------------
Slot Sensor Temperature Lower Warning Alarm Shutdown
1 hotspot 1 51 0 92 102 NA
1 hotspot 2 55 0 98 108 NA
1 hotspot 3 32 -20 63 70 NA
1 hotspot 4 25 0 110 130 135
not sure where those 4 hotspots are.
HP5900, Comware Version 7.1.045, R2311P04
in an office environment (guessing 24C or something)
]display environment
System temperature information (degree centigrade):
-------------------------------------------------------------------------------
Sensor Temperature LowerLimit WarningLimit AlarmLimit ShutdownLimit
hotspot 1 36 0 50 55 NA
hotspot 2 46 0 58 63 NA
so, different limits of course dependig on the ASICs and CPUs on the diffenrent boards.
Hope this helps.
Regards